    The following is from the June 2009 IMCA Safety Flash:

    Electric Shock Near-Miss

    A member has reported an incident in which an employee sustained an electrical shock whilst re-routing a work class remotely operated vehicle (ROV) tether. The ROV and tether management system (TMS) have separate electrical supplies and separate electrical circuits. At no point in the operation was power ever supplied to the ROV through the soft tether either deliberately or accidentally.

    The ROV electrical power was isolated and locked off in order to allow ROV personnel to remove the tether from the vehicle. The TMS power supply was not locked off, in order to allow spooling to take place. Prior to removing the tether from the ROV, technicians used the correct test equipment and earthing equipment to ensure that there was no electrical power at the topside power distribution junction box and at the subsea ROV junction box.

    During the rerouting operation the TMS single phase power was energised to pay out the tether. At this point an ROV technician received an electric shock to his wrist between his glove and coverall. On investigation it was found that, with the TMS single phase power energised, 360V AC was seen on the vehicle end of the ROV umbilical instrument conductors. When the TMS single phase was switched off it was then noticed the 360V AC had dropped to zero volts. All of the wiring was as per specification, no wires were crossed.

    No injury was sustained and no medical treatment was required.

    Following investigation, the following points were noted:
    – A toolbox talk was carried out where the operation and safety aspects were discussed;
    – The immediate cause of the electric shock was the ROV technician coming into contact with a conductor at the end of the ROV tether;
    – This conductor, whilst isolated from a direct power source, was identified as having an induced voltage present. The voltage was induced in the main lift umbilical on the deck winch;
    – One of the functions of the earthing equipment was to tie conductors to earth and eliminate any induced voltage that may be present. On this occasion, two of the clips of the earthing equipment had become dislodged. The ‘crocodile’ clip arrangement was found not to be a secure method of attaching such a safety critical device;
    – Some of the persons involved with this earthing equipment had not fully understood the criticality of the equipment, particularly in the case of high voltage (3000V) and a long umbilical (3300m). Nevertheless, this equipment was correctly used and all appropriate procedures were followed;
    – Personnel needed to be more aware of induced voltages and their potential to be fatal. The umbilical manufacturer confirmed that the induced voltage found in this tether was potentially fatal rather than superficial as some of the persons involved had thought.

    The company has made the follow recommendations and corrective actions:
    – Improve design of earthing equipment in such a way as to remove the possibility of inadvertent disconnection;
    – Follow up with the manufacturer to include start up, induced voltage and isolation in training course material;
    – Ensure all personnel working on work class ROV systems have completed HV training courses;

    Ensure signage is posted at all high voltage junction boxes warning of HV dangers and necessity to use appropriate earthing equipment.

    #23607
    Ray Shields
    Participant

    Ive seen this done a few times, getting a belt off a "dead" conductor. People forget an umbilical is a big coil.

    Of course if everyone had followed the procedures and earthed all of the disconnected wires – but who bothers doing that? Its a lot of hassle? Its only a 5 minute job…

    Remember the same goes when you 5kV Insulation test an umbilical, you test one wire, the others will get charged up.

    Wonder if they teach this at ROV Training Schools?

    #23608
    Savante
    Participant

    POOR TRAINING AND EDU-MA-CATION.

    #23609
    Ray Shields
    Participant

    POOR TRAINING AND EDU-MA-CATION.

    I would disagree, I have seen people who have been trained and educated on this and still get belts.

    Poor Supervision. Supervisor should have stopped them and made them do it properly.