Protecting divers from electrical shock

Home Forums ROV ROV Technical Discussions Protecting divers from electrical shock

Viewing 7 posts - 1 through 7 (of 7 total)
  • Author
    Posts
  • #6775
    Svein Joar Vareberg
    Participant

    Interested to know what safeguards are normally used when divers are in the water with a HV ROV.

    IMCA D045 specs a maximum 20ms trip delay for RCD/isometer, which is hard to guarantee, and also seems aimed at smaller equipment types/lower voltages.

    #35314
    liddelljohn
    Participant

    As you state most diver support is done with smaller /medium ROVs , Mohicans , panthers , Tigers etc and usually no special precautions other than reasonable separation from diver is made ,,,

    #35315
    T-Boy
    Participant

    We wrap the divers in black neoprene and make them wear really silly underwater shoes…seems to work ok 😆

    #35316
    Alan
    Participant

    Good joke)
    Sea water is a good conductor, but what about fresh water operations?

    #35317
    piper
    Participant

    Very mature of you T-Boy. You might think all people buy your idea of jokes but I know you have no clue what to say and the best thing for you is to pass a joke. The discussion is beyond your comprehension.

    #35318
    timebandit
    Participant

    From my experience with work class HV systems , a LIM system offers no protection to personnel on deck due to the slow reaction time of the system and also the line capacitance of the system has a direct affect on the reaction time.
    So for a diver, best to keep well away unless you have found a system better than the Bender .

    #35319
    Svein Joar Vareberg
    Participant

    Yes we use Bender and also Megacon LIMs, but they use the same principle, injecting DC.
    A full blown earth fault will trip them very fast but for Bender it can be up to 4s response time for a lesser fault (if I remember).

    We also use isolating transformers tho (non-earthed neutral), and cut power supply at the first earth fault.

    Very interesting to hear peoples experience in this area.